Hey, i have a X20SLX806 SafetyCard and im trying to run my motors. I already set two Axis and can see them on the mappCockpit.
Those are the things i already have in my SafetyDesigner. What can i do ? im questioned…..
When i click SafePLC this comes up:
Do you have transfered the grey Automation Studio Project and do you have a online Connection to your grey PLC active in your Automation Studio?
Is the grey PLC in Mode RUN?
Does the IO-Suppy have 24V for the X2X Backplane the X20SLX806 is connected to?
It depends on the Supply Module (X20PLC, X20Buscoppler, X20Busreciever) how the IO-Supply is supplyed. But this has to be present that the X20SLX is working.
Below one of my mistakes I put on the top on my “don’t do that again!“:
I was not able to connect to my SLX because I didn’t connect (as Michael said) 24V to 24 V I/O. In my mind it was enough to apply 24V to the CPU, yup just in my mind.
(Michael’s) Do you have transfered the grey Automation Studio Project and do you have a online Connection to your grey PLC active in your Automation Studio?
(Michael’s) Is the grey PLC in Mode RUN?
2.1) Could you upload SystemDump?
Are you using Mapp Safety? Which version?
3.1) Have you enabled the visualization on the General safety configuration?
3.2) In case you didn’t configure the HMI, We have SfDomain library to connect/transfer/acknowledge Safe LOGIC/SLX
Try to call SfDomainConnect and tell us which Error and StatusID you have