X90 with X67BC8321.L12 and X67IF1121-1 causes service mode RS232 Serial

I have added a X67BC8321.L12 and configure, in AS version 6.7.2.9. I connected a prox sesnor to Port 2 on the bus controller, added a simple ladder to read that input, and a simple output on MF-DO channel 25. Rebuild configuration and transfer to target, no issue, works as expected. I then added a the X67IF1121-1 as shown below.

And from that point forward I go into the dreaded SERV mode. Thankfully I have the non-serial module version on a thumb drive, so I can quickly unbrick the PLC. But what do I need to do to get this program working with the IF1121? FYI this my current setup:

Hi,

can you please share the logger screenshot, or even better a system dump?

Bedt regards!

Hi @Ruben_Rascon ,
you can also call or write and email to our Support in US support.us@br-automation.com

Ciao
Valerio

Looks like my cable is not an X2X compatible–it is D coded (reverse coded) but only 2 wire instead of 4. Will test again when the new cables arrive.

Got a new cable, but same error. This is a B coded 5 pin M12 cable–as per the X67BC8321.L12 and X67IF1121-1 docs. Same error in the logger. How do I get the system dump when unit is in Service Mode?

Hi @Ruben_Rascon ,

First please disable module supervised to your 2 X67 modules:

after that your system will not go to service mode in case one of both modules are not recognized.

After that with SDM or with AS and monitor activated you can see the status of ModuleOk:

If I have understood correctly there is no issue with the first X67 module: X67BC8321.L12. Am I right?

Second, Installed all hw upgrades (theoretically the latest is the greatest :slight_smile: ):

Regarding SystemDump, you have to enable SDM + Web Server in your prj and disable the Authentication (as first step):

You are already connected to the target so you can open SDM (System Diagnostics Manager) form AS menu (Tools > System Diagnostics Manager):

When you click on Hardware you will see:

Back on SytemDump, click on the area below:

Check your Downloads folder:

Please upload that.
SDM is running even if the target is in service mode.

Regarding the connections:

X67BC8321.L12 | B&R Industrial Automation

Datasheet X67BC8321.L12 | B&R Industrial Automation

X67IF1121-1 | B&R Industrial Automation

Datasheet X67IF1121-1 | B&R Industrial Automation double check section:

  • 2.2 LED status indicators and section
  • 2.3 Connection elements

Thanks
Ciao
Valerio

Valerio this has been extremely helpful! I did indeed see the 8321 show True for Module OK, whereas the 1121 is False. My X90 version appears to be out of date. So I will update and see if that fixes my issue. The cables I have do match what the docs require, so I think I am good there. Will report back after I update the X90.

If the hw upgrade doesn’t fix the problem, Ruben, disconnect all sensors and double check:

  1. X2X cable
  2. 24V cable
  3. module

Ciao
Valerio

I downloaded the HW upgrade to get me to 1.6.1. However when I open the Upgrade window it is not listed in my local directory (where I have all of my B and R Upgrades). The other items appear but not the HM file.

If I try to use the B&R website, I always the following error:

Thoughts?

Hi @Ruben_Rascon ,
I think we have other priority today :slight_smile: than tools → Upgrades, please download the file from our website: V6.0 HW Upgrade (X90CP174.48-00) | B&R Industrial Automation

Once you have the file, select the second tab ‘Local’ on tools > Upgardes

if the installation is completed in correct way you see a folder with the name of your X90 in the Upgrades folder:

Ciao
Valerio

The cable was the issue. Now we have comms to the 1121. We have now connected our Trimble NAV 900 GPS unit and we have our next issue. All of the NMEA strings that come from the GPS unit start with a $. The 1121 gives us an 8079 error (this is when using the Receiver program and modifying the appropriate settings). As I understand it, this is a reserved or special character in the B and R world. How can we get around this? Here is a screenshot of the status error:

Here is a sample of the data from the NAV900:

$GPGGA,193008.60,3842.038133,N,09031.102976,W,1,23,0.8,141.055,M,-33.569,M,56
$GPVTG,000.0,T,000.02,N,000.04,K,A
46
$GPGGA,193008.80,3842.038134,N,09031.102975,W,1,24,0.8,141.053,M,-33.569,M,5D
$GPVTG,000.0,T,000.01,N,000.02,K,A
43
$GPGGA,193009.00,3842.038133,N,09031.102976,W,1,23,0.8,141.054,M,-33.569,M,50
$GPVTG,000.0,T,000.02,N,000.04,K,A
46
$GPGGA,193009.20,3842.038133,N,09031.102975,W,1,24,0.8,141.052,M,-33.569,M,50
$GPVTG,000.0,T,000.02,N,000.04,K,A
46
$GPGGA,193009.40,3842.038133,N,09031.102975,W,1,24,0.8,141.052,M,-33.569,M,56
$GPVTG,000.0,T,000.03,N,000.06,K,A
45
$GPGGA,193009.60,3842.038133,N,09031.102974,W,1,23,0.8,141.053,M,-33.569,M,53
$GPVTG,000.0,T,000.02,N,000.04,K,A
46
$GPGGA,193009.80,3842.038133,N,09031.102973,W,1,23,0.8,141.051,M,-33.569,M,58
$GPVTG,000.0,T,000.02,N,000.03,K,A
41
$GPGGA,193010.00,3842.038134,N,09031.102969,W,1,24,0.7,141.043,M,-33.569,M,5F
$GPVTG,000.0,T,000.01,N,000.02,K,A
43

As first step, you don’t need to connect PVs (process variables), but just activate monitor mode:

Ciao
Valerio

I did try changing the Function Model from stream to flat stream and cyclic stream, but then no data arrives. BTW to test for data arrival I can physically disconnect the serial cable, and when disconnected Reciever.step does not change from FRM_RBUF to FRM_READ rapidly. This rapid switching only occurs when Function model is set to stream and cable connected. I also tried changing the AsynSize from 24 to 28 with no improvement, but did not try other values here. I will try turning on the Serial Interface 1 error status info when I am back at the workspace next Monday. Thank you again for your prompts suggestions!