Error in AS, Automation Runtime is not supported

I am using automation studio 6.1.. I upload the program plc but this error getting. Can you help me please.
Runtime version in plc- k.4.34

Hi,

it looks like you dont have a Runtime specified… have a look at “Project->Change Runtime Version”.

There should be a Runtime specified.

When do you get the error? right away when you click on “transfer” or “build/Rebuild”?

1 Like

It seems as this project was originally done in AS4.x and then upgraded to AS6.x
You chosen AR version from AS4.x - K4.34 - is not supported in AS6.x
AS6.x only supports AR versions 6.x
Due to this please use “Tools/upgrades” to download an AR version suitable for your PLC