Hello, I have problem with connection between AS 4.12 and APC 3100. I can´t see APC in online settings in AS, but in app Wireshark i can see IP for APC. I have correct IP in AS for ETH 1 or ETH 2 but nothing found. If I ping from APC to my notebook everything is OK but opposite ping is not possible. Have I make same changes on APC or allow access for communication? Thank you for your advice.
Hello,
in recent AS/AR versions (I think 4.90 and newer) the SNMP protocol is disabled in the ethernet adapter configuration in Automation Studio.
A connection from your notebook to the APC3100 should be possible, but you have to enter the IP address manually.
The browsing function uses SNMP - as mentioned, this needs to be enabled and transfered to the APC.
Yes i know but i can´t find APC for the first time. I know IP address (from wireshark) but if i enter address manually and try connection, I am still offline. Our APC is powered for the first time.
Hi Vojtech
Did you already install a project on the system?
If not, please follow the thread from @austin.carpenter below:
Good luck!
Jan
Hi Vojtech, what is status of your topic? can you share with us your solution if there is any?
Closed due to inactivity. Feel free to reopen the topic if you have any updates or new questions.
Sorry for my inactivity, i was on holiday. Everything works. Problem was solved by USB installing. I made USB project installation in AS and install on APC during boot.
Thanks for update